- Code: Select all
! RadLoTempHydrCoolTower.idf
!
! Basic file description: 1 story building divided into 3 interior conditioned zones. Roof with no plenum.
! No ground contact with floor.
!
! Highlights: Hydronic low temperature radiant system heats and cools
! "Chilled" water provided only by a cooling tower
!
! Simulation Location/Run: CHICAGO_IL_USA_WMO_725300, 2 design days, 1 run period,
! Run Control executes the design days only.
!
! Location: Chicago, IL
!
! Design Days: CHICAGO_IL_USA Annual Heating 99%, MaxDB=-17.3°C
! CHICAGO_IL_USA Annual Cooling DRY (DB=>MWB) 1%, MaxDB=31.5°C MWB=10°C
!
! Run Period (Weather File): none
!
! Run Control: No Zone or System sizing required (design days only, see RUN CONTROL object)
!
! Building: Single floor rectangular L-shaped building 40 ft south wall, 40 ft west wall, zone height 10 feet.
! There is a single window in the West Zone south wall. The walls are 1 in stucco over 4 in common brick
! and gypboard. The roof is a built up roof with 1/2 in stone over 3/8 in felt over 1 in dense insulation
! supported by 2 in heavy weight concrete. The window is single pane 3mm clear.
! The window to wall ratio is approxomately 0.07.
!
! The building is oriented due north.
!
! Floor Area: 130.1 m2 (1403 ft2)
! Number of Stories: 1
!
! Zone Description Details:
!
! (0,12.192,0) (9.144,12.192,0)
! ________________________________
! | |
! | |
! | |
! | |
! | North |
! | |
! | |
! | (6.096,6.096,0) |
! |________________________________|____________ (12.192,6.069,0)
! | (0,6.096,0) | (9.144,6.096,0) |
! | | |
! | | |
! | | |
! | West | East | window = *
! | | |
! | | |
! | | |
! |___**************___|________________________|
!
! (0,0,0) (6.069,0,0) (12.192,0,0)
Report: Component Sizing Summary
================================
For: Entire Facility
Timestamp: 2012-12-29 21:38:18
ZoneHVAC:LowTemperatureRadiant:VariableFlow
Maximum Hot Water Flow [m3/s] Maximum Cold Water Flow [m3/s] Hydronic Tubing Length [m]
WEST ZONE RADIANT FLOOR 0.000139 0.000603 247.74
EAST ZONE RADIANT FLOOR 0.000142 0.000544 247.74
NORTH ZONE RADIANT FLOOR 0.000205 0.000735 371.61
PlantLoop
Maximum Loop Flow Rate [m3/s] Plant Loop Volume [m3]
CHILLED WATER LOOP 0.001881 1.41
HOT WATER LOOP 0.000486 0.364602
Pump:VariableSpeed
Rated Flow Rate [m3/s] Rated Power Consumption [W]
CIRC PUMP 0.001881 480.69
HW CIRC PUMP 0.000486 124.20
Report: Adaptive Comfort Summary
================================
For: Entire Facility
Timestamp: 2012-12-29 21:38:18
Time Not Meeting the Adaptive Comfort Models during Occupied Hours
ASHRAE55 90% Acceptability Limits [Hours] ASHRAE55 80% Acceptability Limits [Hours] CEN15251 Category I Acceptability Limits [Hours] CEN15251 Category II Acceptability Limits [Hours] CEN15251 Category III Acceptability Limits [Hours]